# MOBOTIX Thermal Validation - Simulated App Acceptance Test

**URL:** <https://community.mobotix.com/t/mobotix-thermal-validation-simulated-app-acceptance-test/10090>\
**Category:** MOBOTIX Apps\
**Created:** [November 24, 2025, 7:54pm UTC](https://community.mobotix.com/t/mobotix-thermal-validation-simulated-app-acceptance-test/10090 "2025-11-24T19:54:52Z")\
**Posts on this page:** 1\
**Page:** 1

<div class="post-metadata">

**Author:** ![Mx-PhilippH](https://yyz2.discourse-cdn.com/flex030/user_avatar/community.mobotix.com/mx-philipph/32/10382_2.png) [@Mx-PhilippH](https://community.mobotix.com/u/Mx-PhilippH)\
**Post date:** [November 24, 2025, 7:54pm UTC](https://community.mobotix.com/t/mobotix-thermal-validation-simulated-app-acceptance-test/10090/1 "2025-11-24T19:54:52Z")

</div>

**Purpose**

The MOBOTIX Thermal Validation App is designed to distinguish real temperature events from reflections, moving heat sources or transient disturbances. It enhances the reliability of _Thermal Image Fire Detection (TIFD)_ in dynamic environments such as recycling plants, waste bunkers, or industrial halls with machinery movement. For a detailed introduction to the functions and general conditions of the MOBOTIX Thermal Validation App, please refer to the corresponding app documentation.

This checklist describes a best-practice **simulated** acceptance procedure to verify that the app and the TIFD system operate correctly with a suitable radiating reference source under controlled, simulated test conditions.

**Preparation**

- Ensure the TIFD system and the MOBOTIX Thermal Validation App are properly configured and active.
- Prepare a radiating reference source (e.g., blackbody radiator or equivalent) that meets the specified test conditions for accurate temperature measurement (minimum 3×3 pixel spot coverage in the test distance).
- Set the reference source to remain stable and stationary during the entire test.
- Note the configured alarm threshold temperature(s) (e.g., 80 °C).

**1) Setup**

- Position the reference source within the camera’s field of view but cover it completely so it cannot be detected by the TIFD.
- Begin the heating process of the reference source, targeting the configured threshold temperature.

**2) Partial Exposure**

- As heating begins, partially uncover (≈50%) the reference source so that the TIFD can partially measure its thermal radiation.
- Continue heating until the measured temperature in the TIFD image reaches the configured threshold (e.g., pre-alarm threshold 80 °C).

**3) Learning Phase**

- Once the threshold temperature is reached, keep the setup unchanged for 20–25 seconds to allow the Validation App to analyze the heat signature.
- During this period, confirm that the app displays a detected temperature spot within the defined measurement area in the TIFD’s live image, indicating that the object is recognized as a relevant hotspot.

**4) Growth Simulation**

- After the learning phase, fully uncover the reference source to simulate the natural growth of a hotspot.
- Observe the TIFD and confirm that the system immediately triggers the configured alarm (visual and/or via output interface).

**Expected Results**

- The hotspot is correctly detected and displayed after the learning phase.
- When the heat signature expands, the Thermal Validation App confirms the event being valid and the TIFD triggers the alarm according to configuration.
- No false alarms occur during static or partially covered phases.